Are you asking about multiple circuits in a raceway? For individual cables identification is generally not required when it is evident where the conductors originate.How come you must group all associated conductors for a specific circuit but you don’t necessarily need to identify it’s circuit number(number tags etc)
Imo its not evident it you have multiple conductors (circuits) in a conduitAre you asking about multiple circuits in a raceway? For individual cables identification is generally not required when it is evident where the conductors originate.
It's not and the NEC therefore requires that the individual circuits be marked or grouped to indicate which conductors go together. You can bundle them with tape, use a cable tie, mark the individual conductors with wire markers, etc.Imo its not evident it you have multiple conductors (circuits) in a conduit