Re: "Grouping" How would you interpet this 400amp
I too have used the back KO's to feed the panel out of a meter, but I have to use only the middle KO or teh utility get's alittle upset.
As far as mositure freezing in the nipple. 300.7 will clearly solve that problem if it is followed.
Haveing a service disconnect on the outside of the building and then have a main breaker panel inside would be a violation of grouping.
I would belive the intent is the same as for the six movments of the hand requirment, which would require the disconnects to be close enough to be reached, without much movment of the operator to another location, and should be within sight of each other.
Amptech:
If you supply an outbuilding why would you install a 320/400 meter then install a disconnect to feed the outbuilding?
first if the service conductors do not enter a building they do not need a disconnect, second you will still need a main disconnect that is service rated, at the outbuilding if you have over six circuits! ( which I think you would with a 200 amp panel)
Why not just use the second set of lugs and run to the out building and hit a main breaker panel as we are allowed by the exception #3 in 230.40?
Then this feed is a service conductor feed which only has to meet the requirment's of 230. Which would mean that these conductors are service entrance conductors. Only three wires would be ran and you would bond to the grounded conductor as 250.142 allows. Install a ground rod or two and be done which a ground rod would have to be installed anyway.