Re: "Grouping" How would you interpet this 400amp
If the service, the single metering point served by the utility, is located on one building and you are serving 2 or more buildings from this service, how would you "group" the service disconnects? If you do as allenwayne said and back to back a MB loadcenter with the meterbase and then run 3 wire from the load side of the meterbase to a MB loadcenter in a separate building there could not be any other metal conductive paths between the buildings. If there were you would need a 4th wire. If the utility used one transformer to provide 2 separate drops to the 2 buildings each with their own separate service and metering it is a different story.
If the service, the single metering point served by the utility, is located on one building and you are serving 2 or more buildings from this service, how would you "group" the service disconnects? If you do as allenwayne said and back to back a MB loadcenter with the meterbase and then run 3 wire from the load side of the meterbase to a MB loadcenter in a separate building there could not be any other metal conductive paths between the buildings. If there were you would need a 4th wire. If the utility used one transformer to provide 2 separate drops to the 2 buildings each with their own separate service and metering it is a different story.