paulgarett
Member
- Location
- San Rafael, CA
All phase conductors (10 AWG THHN) for five 10 hp, 480 volt motors are grouped in the same raceway, 1" PVC, for about 100 feet and end at a junction box. From the junction box flex is run to each individual motor.
If these motors are on continuously, would grouping 15 conductors (5 motors x 3 phase) plus ground in the same raceway create heating and cause the motor starters to trip?
One of these motors start-up current is between 75-90 Amps. Their running current is about 14 amps. The five motors are on timers so they don't come on at the same time. One comes on immediately, five seconds later 2 more come on, five more seconds, 2 more come on for a total of five. The start-up current is quite large. The 10 AWG was not sized for 75-90 amps. I am worried the magnetic induction of the conductors in the raceway are causing the motor starters t to trip.
If these motors are on continuously, would grouping 15 conductors (5 motors x 3 phase) plus ground in the same raceway create heating and cause the motor starters to trip?
One of these motors start-up current is between 75-90 Amps. Their running current is about 14 amps. The five motors are on timers so they don't come on at the same time. One comes on immediately, five seconds later 2 more come on, five more seconds, 2 more come on for a total of five. The start-up current is quite large. The 10 AWG was not sized for 75-90 amps. I am worried the magnetic induction of the conductors in the raceway are causing the motor starters t to trip.