Grouping Multiple Motor Conductors in Same Raceway
paulgarett
San Rafael, CA
All phase conductors (10 AWG THHN) for five 10 hp, 480 volt motors are grouped in the same raceway, 1" PVC, for about 100 feet and end at a junction box. From the junction box flex is run to each individual motor.
If these motors are on continuously, would grouping 15 conductors (5 motors x 3 phase) plus ground in the same raceway create heating and cause the motor starters to trip?
One of these motors start-up current is between 75-90 Amps. Their running current is about 14 amps. The five motors are on timers so they don't come on at the same time. One comes on immediately, five seconds later 2 more come on, five more seconds, 2 more come on for a total of five. The start-up current is quite large. The 10 AWG was not sized for 75-90 amps. I am worried the magnetic induction of the conductors in the raceway are causing the motor starters t to trip.
Derating for 40C ambient and multiple conductors still give you 15.4A on a #10AWG THHN, so I would say there is no problem. Wiring is not sized for inrush current, which is about 600% in your case, nothing unusual. (Should you have these motors on Adjustable Speed Drives, then you may see problems, but those would be a set of different issues, not (just) overload.)