Is it good idea to group the AC main PV disco that is tapped from line side of the building main service disconnect with the building main service disconnect or not?
Does 705.31 not cover this ?
Why would it not? I always group them when and where I can.Is it good idea to group the AC main PV disco that is tapped from line side of the building main service disconnect with the building main service disconnect or not?
Why would it not? I always group them when and where I can.
If I read it correctly you are saying why you think they might not need to be grouped rather than any reason why they shouldn't. Most of the AHJs I deal with want them to be grouped if it is possible to do so, and I don't know of any reason why they shouldn't be.See post #4. What do you think?
I have plans that show main service disco is inside the building wall and right opposite to the main service disco wall outside is the AC PV disco.
When given comment to group them was told that NEC 2017 section 230.71(A) references 230.40 exceptions 1,2,3,4 or 5 and says for each set of service entrance conductors permitted in 230.40 exceptions need no more than six circuit breakers.
NEC 2017 section 230.72(A) says two to six disconnects in 230.71 need to be grouped.
Since there are two separate service entrance conductors one for solar AC disconnect and the other for main service building disconnect the two do not need to be grouped.
Does anyone agree with that?[\B]
If I read it correctly you are saying why you think they might not need to be grouped rather than any reason why they shouldn't. Most of the AHJs I deal with want them to be grouped if it is possible to do so, and I don't know of any reason why they shouldn't be.
The ones I've seen will have in addition to that fused disconnect required within ten ft of the line side tap, disconnect(s) on outside within sight and a few feet of meter. Those disconnects are usually grouped. I suppose if 2020 requirements are in place the PV disconnect and the service disconnect are grouped near each other.I have plans that show main service disco is inside the building wall and right opposite to the main service disco wall outside is the AC PV disco.
When given comment to group them was told that NEC 2017 section 230.71(A) references 230.40 exceptions 1,2,3,4 or 5 and says for each set of service entrance conductors permitted in 230.40 exceptions need no more than six circuit breakers.
NEC 2017 section 230.72(A) says two to six disconnects in 230.71 need to be grouped.
Since there are two separate service entrance conductors one for solar AC disconnect and the other for main service building disconnect the two do not need to be grouped.
Does anyone agree with that?
The ones I've seen will have in addition to that fused disconnect required within ten ft of the line side tap, disconnect(s) on outside within sight and a few feet of meter. Those disconnects are usually grouped. I suppose if 2020 requirements are in place the PV disconnect and the service disconnect are grouped near each other.
The AHJ's I deal with consider the 10' rule in 705.31 to mean the maximum length of conductors.What I don’t like is what I call smart plans ones that reviewer has to scratch their head and say uh oh this is unusual because they do place two discos next to each other But they place it on opposite sides of building one inside wall and one outside wall of building but still within 10 feet
What do you do then? What does 10 feet measured from cable or actual person walking to disconnect? No guidance at all.
I still don't get what you are driving at, but it's OK.See bolded part thats why.
You struggle with this a lot. Yes there are things in the code that are vague or could be interpreted different ways. Just make a decision and move on.What I don’t like is what I call smart plans ones that reviewer has to scratch their head and say uh oh this is unusual because they do place two discos next to each other But they place it on opposite sides of building one inside wall and one outside wall of building but still within 10 feet
What do you do then? What does 10 feet measured from cable or actual person walking to disconnect? No guidance at all.
You struggle with this a lot. Yes there are things in the code that are vague or could be interpreted different ways. Just make a decision and move on.
Personally, if someone asked me how I came to a decision, I would much prefer to tell them that is the way I read the words rather than that's what people on an internet forum said.
How would you see the measurement for reasoning of electrical codes, if you have the 2 disconnect only 2ft apart but you run a conduit to get around an obstacle ten ft? Is that 2ft or 10ft? To know first start with what is reason for a given measurement limitation?What I don’t like is what I call smart plans ones that reviewer has to scratch their head and say uh oh this is unusual because they do place two discos next to each other But they place it on opposite sides of building one inside wall and one outside wall of building but still within 10 feet
What do you do then? What does 10 feet measured from cable or actual person walking to disconnect? No guidance at all.
Just to be clear: There are lots of super knowledgeable people on here. I dont mean to diminish that....But unfortunately I tell some people about an issue that was discussed here and expect that since it was from MH forum so it should have some serious weight and sometimes they are like, "dont know that Mike Holt forurm....".......rather than that's what people on an internet forum said.
I'm pretty sure that most AHJs would interpret that exception to apply only to multiple service entrance conductors from the same service, i.e., the utility.Not really there are times its in the code not just opinion helps what most think though.
Do you think 230.40 exception no 2 would apply and make the PV ac disco and the building main grouped? Only thing if PV system would supply separate loads or not 230.40 exception no 2 apply or not
I still don't get what you are driving at, but it's OK.