I need to supply a detached garage with 150amp service. Here is my question. The garage is located 6 feet from the existing service. I set up for a heavy up from 200 to 350 with the power company. A dual lug meter allready exists with the 200 amp service for the dwelling. I can't find any codes NOT allowing me to come frome the dual lug meter directly to the garage supplying a 150 amp main breaker panel (means of disconnect nearest point of entry). Keeping in mind the feeder will not be on the load side of the service disconnecting means and it serves a second structure on the same property under one owner (225.30) Can anyone help me understand the code and how it applies to this application. In the past I have come from the meter base with a second set of service conductors to a disconnect next to the service equipment then to the other structure. Keeping my disconnects grouped together (225.34) 