So a couple weeks ago I was dispatched to troubleshoot a tripping circuit breaker at a local parcel delivery company's distribution center/warehouse. The breaker is supplying exterior lights.
There are actually two circuits supplying outside lights. The first one (20A 120V) supplies a pair of 250W HPS wallpacks. It also provides power for the control circuitry - photocell and contactor. This breaker has reportedly never tripped and has always functioned just fine. The second breaker (also 20 A 120 V) was the problem. It supplies a total of (4) 250 W HPS wallpacks, (1) 70W HPS Wallpack, and one MH flood (don't recall the lamp wattage, but the sticker inside the fixture said it should pull roughly 4 amps at 120V).
Occasionally when the delivery crew showed up in the morning, the lights supplied by the 2nd breaker would be off, and they'd find the breaker tripped. They would reset it, and no problems for a few more days. Then, poof, magically tripped overnight again. That's when they called.
The first time I went out, it was toward the end of the day and I didn't have a whole lot of time to troubleshoot stuff. The breaker wouldn't trip for me. There were no indications of ground fault or short. The circuit pulled about 15 amps, which is about what I expected. Being short on time, I replaced the rather old breaker with a brand new one off the van.
About a week later, they called back and said it was tripped again. I went out (with more time) and opened up all the exterior lights, looking for things like moisture infiltration or burnt-up wire nuts that might be banging around against the inside of the grounded fixture when it got windy or something. Found nothin' except one of the HPS ballasts was looking fairly cooked and crispy. I replaced it. Still no ground faults or anything on the whole circuit, and it was still pulling about 15 amps or so. Nothing definitive yet.
Now just today they called AGAIN saying their breaker was tripped. I'm going there first thing Monday morning. It was pretty windy and rainy last night and that may have had something to do with it. But I'm pretty sure the weather was nice and clear the last few times I've been out.
At this point I don't really know where to go next, short of hooking up my recording meter for a night or two and seeing what exactly is going on when the breaker trips. So does anyone have any suggestions or ideas for me? Sorry for the long post.
There are actually two circuits supplying outside lights. The first one (20A 120V) supplies a pair of 250W HPS wallpacks. It also provides power for the control circuitry - photocell and contactor. This breaker has reportedly never tripped and has always functioned just fine. The second breaker (also 20 A 120 V) was the problem. It supplies a total of (4) 250 W HPS wallpacks, (1) 70W HPS Wallpack, and one MH flood (don't recall the lamp wattage, but the sticker inside the fixture said it should pull roughly 4 amps at 120V).
Occasionally when the delivery crew showed up in the morning, the lights supplied by the 2nd breaker would be off, and they'd find the breaker tripped. They would reset it, and no problems for a few more days. Then, poof, magically tripped overnight again. That's when they called.
The first time I went out, it was toward the end of the day and I didn't have a whole lot of time to troubleshoot stuff. The breaker wouldn't trip for me. There were no indications of ground fault or short. The circuit pulled about 15 amps, which is about what I expected. Being short on time, I replaced the rather old breaker with a brand new one off the van.
About a week later, they called back and said it was tripped again. I went out (with more time) and opened up all the exterior lights, looking for things like moisture infiltration or burnt-up wire nuts that might be banging around against the inside of the grounded fixture when it got windy or something. Found nothin' except one of the HPS ballasts was looking fairly cooked and crispy. I replaced it. Still no ground faults or anything on the whole circuit, and it was still pulling about 15 amps or so. Nothing definitive yet.
Now just today they called AGAIN saying their breaker was tripped. I'm going there first thing Monday morning. It was pretty windy and rainy last night and that may have had something to do with it. But I'm pretty sure the weather was nice and clear the last few times I've been out.
At this point I don't really know where to go next, short of hooking up my recording meter for a night or two and seeing what exactly is going on when the breaker trips. So does anyone have any suggestions or ideas for me? Sorry for the long post.