If your recording meter has clamps for both hot and neutral, do measure both, as that'll determine if your overcurrent is phase - neutral or phase - ground.
You're actually lucky (or perhaps just well equipped) to have a recording meter, they are reasonably rare in the contracting community, yet without one, tracing this type of mischief is harder than it need be.
And having reread the original post, I do not agree that the breaker is tripping "by magic"; theres always a reason for these things, albeit sometimes the reasons are a tad difficult to come by
Yep the recording meter has served me well in the past. Troubleshot a weird issue at the hospital with it a few years ago, and then an even weirder issue at the Aquarium with it last year. I just hope to death that no one formatted the hard drive of the computer with the uploading software on it.
Could be the same as having a loose wire. The breaker could be going out on thermal overload.
I had a situation where another elect. wanted to replace a panel that was only 1 year old. Every thing worked fine until the heat strips in the HVAC unit would run for about 20min. then the main would trip. PhA in the main was loose. It wasn't loose enough to arc but was loose enough to cause the main to heat up and trip on thermal. Torqued it down and it has been good for three years now.
Makes sense I suppose.... I'll tighten some things down.