I believe this is correct
using THWN I have 12 conductors to size a gutter
3) 4/0 - 3 X .642 = 1.926
6) 2/0 - 6 X .532 = 3.192
3) #2 - 3 X .352 = 1.056
total 6.174
6" X 6" = 36sq in X 20% = 7.2
So a 6X6 gutter would be the correct size
I'm a resi so dont batter me too hard