A 12"x12"x10' Trough. With (51) Current Carrying Conductors. None are a continious Load or lighting circuits.
Was Told max amperage could only be 9.

How I see to do this.
1) Article 110-14-C
2) Table 310.16 #12 THHN at 90 degree 30A
3) Article 366-22 20% fill
Equals 28.80 #12 is .0133
4) Table 310.15(B)(2)(A) Adjustment Factors.
5) Annex B Table 310.11 Adjustment Factors with Diveristy.
6) Which comes to 15A. Then able to go to the next breaker size being a 20A Breaker.


If I am wrong how do you go about this issue.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Assuming a metal wireway see 376.22(B). Your derating factor is 35%. You can't use the "diversity factors" without engineering supervision.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you had an adjusted ampacity of 15 amps then that would be the maximum size of the OCPD since it's a standard size. Also if those circuits contain multi-receptacles then you cannot use the next size up rule.
 