I don't think the voltage drop would be the real issue. I mean, on a 50 foot run of 12 AWG, how much voltage drop would the last inch done in 14AWG cause?
I think the real issue is the physical compromise of the connection. I don't think the math supports a few thousandths of an inch of 4 strands of stranded wire being taken out of the picture as being a voltage drop issue. Remember, the decreased diameter only exists from the cut to the point where the conductor is screwed or bolted to the connector. What's that, maybe 1/8" or less?
Voltage drop through one inch of conductor is not the issue, when conductor is increased in size because of voltage drop, sometimes you have a conductor size larger than the terminations will accept. Even if you trim off some strands to make the termination, you probably will not see any significant voltage drop across the termination. This assumes you don't trim the conductor so much that you effectively have too small of a conductor making up the termination.
Maybe I am saying the same thing you are saying.
I realize this practice is considered a "NO - NO" and does look like hackwork, and I don't make it a habit to do this myself, but I would also like to see reasons not to do it that has some scientific basis behind it. Lug not being listed is the easy way out, I want a better reason than that, like 'we tried to list it for that, but because of.....we could not get it listed.