half inch emt with # 8
hardworker
For a number of reasons, I am forced to use an existing half inch emt run that feeds an rooftop a/c condenser. I need to run two conductors of #8 for a 40amp circuit. I have three 90 degree elbows in the 70ft. run, so the pull might get tight. Will code allow a smaller ground than #8?
for a number of reasons, i am forced to use an existing half inch emt run that feeds an rooftop a/c condenser. I need to run two conductors of #8 for a 40amp circuit. I have three 90 degree elbows in the 70ft. Run, so the pull might get tight. Will code allow a smaller ground than #8?
250.122.......
The emt changes to seal tight before it passes through the roof, so using the conduit as ground won't work. Can I use #12 or #10 as ground? Do you think three conductors of #8 will pull?
Yes, (2) 8's and a 10 will go in a 1/2" assuming THWN
Is there a box at the changeover to flex. If so, just ground from there to unit, not the whole run.
Yes there is a box, so grounding from it to the unit is an option. Does code allow the #10 to be used as ground?
Article 350 of ANSI/NFPA 70, "National Electrical Code" (NEC).
Where terminated in fittings investigated for grounding and where installed with not more than 6 ft (total length) in any ground return path, liquid-tight flexible metal conduit in the 3/8 and 1/2 (12 and 16) trade sizes is suitable for grounding where used on circuits rated 20 A or less, and the 3/4, 1 and 1-1/4 (21, 27 and 35) trade sizes are suitable for grounding where used on circuits rated 60 A or less. See Conduit Fittings (DWTT) with respect to fittings suitable as a grounding means.
The following are not considered to be suitable as a grounding means:
1. The 1-1/2 (41) and larger trade sizes.
2. The 3/8 and 1/2 (12 and 16) trade sizes where used on circuits rated higher than 20 A, or where the total length in the ground return path is greater than 6 ft.
3. The 3/4, 1 and 1-1/4 (21, 27 and 35) trade sizes where used on circuits rated higher than 60 A, or where the total length in the ground return path is greater than 6 ft.
Is the overcurrent device 40 amps or is the load 40 amps?
If feeding an AC unit, a unit requiring 40 amp overcurrent device will often have a load of around 20-25 amps. If you are installing larger than otherwise needed conductors for voltage drop you need to increase equipment ground conductor by a similar increase in size.
You're probably gonna need someone pushing on the other end!
3 #8 THHN = 0.1098 in?
40% on ?" EMT = 0.122 in?
or
3 #8 THHN = 70.83 mm?
40% on ?" EMT = 78 mm?
2 #8's and a#10 for the ground would be a little easier and coderific.
and?:confused: