I cannot comment on any of your local amendments, but New Jersey appears to have adopted the IECC 2015. In IECC 2015, C405.2 Lighting Controls states Lighting systems shall be provided with controls as specified in SEctions C405.2.1, C405.2.2, C405.2.3, C405.2.4, and C405.2.5...but there are exceptions: Lighting Controls are not required for the following:
1) Areas designated as security or emergency areas that are required to be continuously lighted
2) Interior exit stairways, interior exit ramps and exit passageways
3) Emergency Egress lighting that is normally off
This doesn't mean you still cannot use Occupancy sensors for paths of egress though, it just notes that it permits you to not use them. If you do use Occupancy Sensor controls, you are permitted to do the following per IECC C405.2.1.1 which states," Occupant sensor controls in spaces other than warehouses specified in SEction C405.2.1 shall comply with the following: ...(2) Be manual on or controlled to automatically turn the lighting on to not more than 50 percent power. Exception: -Full automatic-on controls shall be permitted to control lighting in public corridors, stairways, restrooms, primary building entrance areas and lobbies, and areas where manual-on operation would endanger the safety or security of the room or building occupants"
Basically, per IECC 2015, you are permitted to use Occupancy Controls and have them turn the lights on to 100% with no problems. You will also want to double check what your local municipality has adopted in addition to what's noted above.