We are installing MCC's for a utility company. Their pumps are controlled from buckets in various MCCs. We have pointed out a potential problem (safety item)with their design. The HOA switches do not truly have a off position. If a limit switch, pressure switch, etc. is closed the pumps will run in the "auto" and/or "off" position. I believe this violates NEC 430-82. The utility says no and does not want to add the additional contact block at the HOA or just a "Hand / Auto" switch in the bucket door to correct the potential hazard.
There is an illusion of being able to turn the pump off at the HOA switch and even though this is not the disconnect (for maintenance) switch, there is the potential of someone turning the Hand-Off-Auto to "Off" and adjusting a shaft or something, believing the pump will not turn on.
Is this really not referenced in the NEC?
There is an illusion of being able to turn the pump off at the HOA switch and even though this is not the disconnect (for maintenance) switch, there is the potential of someone turning the Hand-Off-Auto to "Off" and adjusting a shaft or something, believing the pump will not turn on.
Is this really not referenced in the NEC?