I didn't finish my thought. I don't believe I have been on a job where the incoming water line was copper in at least 10 years. And that includes gold plated spec. government jobs. I believe (just my opinion) that a water pipe could be an optional supplemental ground, but not a, or the primary ground means. In reality I don't really think that, because any plumber who comes in to repair it can replace it with PVC without an electrician being the wiser. Because of that, I believe a water pipe should be treated no differently than a gas pipe. 'bonded where it may become energized.'
IMO the NEC is written to account for the fact that the water pipe may or may not be metallic.
250.50 starts with "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present"
If it is not present - it doesn't need to be used as an electrode.
250.52(A)(1) is metal underground water piping and it describes what requirements are necessary before it is considered an electrode. If those requirements are not met - you don't have a qualifying electrode and you don't have to use it as an electrode.
There is requirement to supplement a water pipe electrode with another electrode - this IMO is because the CMP that wrote that knows that there is a good chance that electrode is likely to be removed, modified, or whatever and will compromise the grounding electrode system if the water pipe is the only electrode present. No other electrodes are required to be supplemented outside of ensuring a driven rod falls below 25 ohms but that is entirely different reasoning for supplementation. Resistance of a water pipe to ground is normally too low to just disregard it compared to many made electrodes.