D Devinp Member Location Broward florida Jun 21, 2017 #1 I have to install a couple handholes my question is what article covers the minimum requirements? And also is there a mi um depth a handhole has to be?
I have to install a couple handholes my question is what article covers the minimum requirements? And also is there a mi um depth a handhole has to be?
steve66 Senior Member Location Illinois Occupation Engineer Jun 22, 2017 #3 jumper said: See article 314 Click to expand... I went to look this up, and I see 314.30 and 314.28. For sizing, you need to determine if any of the conductors #4 or larger. Splices will have to be rated for a wet location, and the manufacturers instructions will probably require a gravel bed under the handhole.
jumper said: See article 314 Click to expand... I went to look this up, and I see 314.30 and 314.28. For sizing, you need to determine if any of the conductors #4 or larger. Splices will have to be rated for a wet location, and the manufacturers instructions will probably require a gravel bed under the handhole.
cowboyjwc Moderator Staff member Location Simi Valley, CA Jun 22, 2017 #4 and depending on where you install it, it may have to be traffic rated.