What says it cannot be done? According to the manufacturer the handle ties are to connect to single pole breakers to one (however the breakers still will trip independently) and they also will make a 2-pole for three 1P positions but nothing more, when asked about multiple circuit breakers the indicated that they do not make such a device / handle? So how would you indicate the breakers serve a multi-wire branch circuit if the manufacturer does not provide a handle tie or ties for multiple breakers, beyond three? The grouping or tying of multiple handles still provides individual breakers to trip and does not create a common trip this is stated in the manufacturers literature so if the grouping is for the purpose of indicating a MWBC to a service contractor what?s the difference of how you tie the handles together to indicate this as long as it is done in a neat manor with a secure device / fitting / strap? Any other recommendations? I tried searching for some but cannot come up with any.