hanging 4' floresent lights off of emt

Status
Not open for further replies.

gilrod

New member
if you run 3/4 emt 30' up in rafters and put twistlock plugs at this hieght. can you hang chain or wire off of conduit to hang your lights down at 20'?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
if you run 3/4 emt 30' up in rafters and put twistlock plugs at this hieght. can you hang chain or wire off of conduit to hang your lights down at 20'?

Are you using the EMT as a raceway (conductors running in it)? If so, then 300.11(B) IMO would prohibit this.
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
You could install a separate EMT and hand light from it, but not the conduit you install as a raceway.
 