I have (85) T5 fluorescent hibay fixtures to hang in a congested area. I am looking for the most efficient and cost effective way to hang them, and am debating between using slotted angle with jackchain, or caddy deck hangers with the deck punch. I have never used the deck hangers and am wondering what others think about them. By the way the ceiling is bar joist and roof deck. Thanks.
 
Nec 2008?

Nec 2008?

DAWGS said:
I have (85) T5 fluorescent hibay fixtures to hang in a congested area. I am looking for the most efficient and cost effective way to hang them, and am debating between using slotted angle with jackchain, or caddy deck hangers with the deck punch. I have never used the deck hangers and am wondering what others think about them. By the way the ceiling is bar joist and roof deck. Thanks.

Is this a retrofit job?

When does the 2008 Code take effect in your area? You may want to check into that prior to starting this project. I am guessing that the current wiring will no longer meet 300.4(E) if it was installed anythng like the fixtures around here. Conduit is usually closer than 1 1/2" from the roof deck.

By replacing the fixtures will your inspector interpret that as a modification to the branch circuit wiring and require you to conform? Will your Caddy Deck Hangers allow the wiring to be more than 1 1/2" from the lowest portion of the roof decking?
 
Also Can Try these

Also Can Try these

Have you ever tried these?

GRIPPLE-INDUSTRIAL.jpg


You can find out more about them on this website (video)

http://www.gripple.com/construction/product.php?prod_id=1/
 
Last edited:
We are adopting 2005 code this month. Virginia stays one code cycle behind. I am running all new conduit, as new fixtures will be 120V, and all old fixtures are 480V and some 277V. Just wondering how quick the caddy deck hangers install, I have never used them.
 
LarryFine said:
One?! :grin: Remember how long we were on the '99?

(Personally, I never complained; it's kept costs down. :wink:)

Larry, don't you like how the supply houses all carry the 2008 code books and not the 05. I could never fiquere that out.
 
DAWGS said:
Larry, don't you like how the supply houses all carry the 2008 code books and not the 05. I could never fiquere that out.
Really! Like Costco, where they put stuff out about 1-1/2 seasons ahead. You can't find summer stuff after about June 1. :roll:
 