Happy Monday, some question today.

Status
Not open for further replies.

Inspectorcliff

Senior Member
Location
Colorado
Is a switch located by the entry to the attic and a light located by the equipment? If it is a drop ceiling in a commerical installation?
As in 210.70.(A) (3).
 
Very good, that is the question. I have some spelling out the definition of Webster’s to what an attic is, and others saying NO Structural ceiling, no attic. I personally agree with you, that if you can remove that many tiles and get to the job, a light and outlet wouldn't be required in my inspection, but it gets really cold here too, so what do I know? Thanks Rob!
 
Suspended ceiling no as in grid with removable tiles..... Drop ceiling?..... I see as let's say hard ceiling with an access to equipment ie. drywall between floors, what are your thoughts? Then yes with (C)
 
210.70(C) should of been could of been

210.70(C) should of been could of been

Is a switch located by the entry to the attic and a light located by the equipment? If it is a drop ceiling in a commerical installation?
As in 210.70.(A) (3).
Back to MOP, Which should have read 210.70.(C), a commerical building, drop ceiling, some sort of support above this d.c. with a electic furnace, boiler, water heater, etc. located up there. I say no, a light switch and an lighting outlet are not required because the area does not meet the requirements of 210.70 (C). :D
 
Yep, I think that is true.

Yep, I think that is true.

Suspended ceiling no as in grid with removable tiles..... Drop ceiling?..... I see as let's say hard ceiling with an access to equipment ie. drywall between floors, what are your thoughts? Then yes with (C)
Yes, then, It would be a cut an dried attic, I think.
 
Back to MOP, Which should have read 210.70.(C), a commerical building, drop ceiling, some sort of support above this d.c. with a electic furnace, boiler, water heater, etc. located up there. I say no, a light switch and an lighting outlet are not required because the area does not meet the requirements of 210.70 (C). :D


I would agree with you.:smile:
 
Cliff,

What you were mentioning is a suspended ceiling...correct? Then No...I have a situation in a hi rise where they dropped the ceiling down from hard deck 2nd floor above with a framed drywall ceiling, 8' high area below the floor area above with access to service a large heat pump and a VAV........They have no passageway to and or work platform let alone a lighting outlet or switch control for the lighting outlet plus no receptacle outlet. Is this an attic or underfloor space according to 210.70(C)?
 
Yes sir, where they put a hard lid in, I definitely call that an attic, even if there were a number of floors above it. To me we are talking a storage area with serviceable equipment. Then the sw. by the entry, the lighting outlet by the equipment and a GFCI outlet all would come in to the picture. That is my opinion.
 