Picked up a job for a local GC that begged me to do it Highland Park TX northern Dallas area. Anyhow whole thing is hard piped in emt, from the panel all the way to the recessed lights. Everything. Its a nightmare. Fast forward to now with AFCI requirements in full swing in inspector even told me "make sure every receptacle and light outlet you add will be AFCI protected". That area has since repealed requirements of conduit only and now allows NM cable wiring. All the circuits are shared neutrals of course and panel is jam packed GE THQL style twin break panel. I am out of ideas to protect 5 outlets and some cans (on three diff circuits). Was hoping that 210.12 A (5) would somehow cut me a break and let me install the receptacle style device at the first outlet I pull power from but it seems the verbiage says otherwise. How do y'all interpret the line "at the first outlet to provide protection for the remaining portion of the branch circuit." Is that first outlet of the existing branch circuit or the first outlet I install "to provide protection to the remaining portion of the branch circuit"
210.12 A (5)
If metal raceway, metal wireways, metal auxiliary gutters, or Type MC, or Type AC cable meeting the applicable requirements of 250.118, with metal boxes, metal conduit bodies, and metal enclosures are installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a listed outlet branch-circuit-type AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
Any feedback is appreciated, gotta tackle this job tomorrow
210.12 A (5)
If metal raceway, metal wireways, metal auxiliary gutters, or Type MC, or Type AC cable meeting the applicable requirements of 250.118, with metal boxes, metal conduit bodies, and metal enclosures are installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a listed outlet branch-circuit-type AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
Any feedback is appreciated, gotta tackle this job tomorrow