I still say they should not be interconnected between apartments.
Here is the requirement for the maximum of 12. It is referring to smoke alarms and does not say wired or wireless. I believe your wireless ones are still limited to 12 because they are not supervised.
NFPA 72 2010 Edition:
29.8.2.2* The interconnection of smoke or heat alarms shall
comply with the following:
(1) Smoke or heat alarms shall not be interconnected in
numbers that exceed the manufacturer?s published instructions.
(2) In no case shall more than 18 initiating devices be interconnected
(of which 12 can be smoke alarms) where the
interconnecting means is not supervised.
(3) In no case shall more than 64 initiating devices be interconnected
(of which 42 can be smoke alarms) where the
interconnecting means is supervised.
Here is the requirement for the maximum of 12. It is referring to smoke alarms and does not say wired or wireless. I believe your wireless ones are still limited to 12 because they are not supervised.
NFPA 72 2010 Edition:
29.8.2.2* The interconnection of smoke or heat alarms shall
comply with the following:
(1) Smoke or heat alarms shall not be interconnected in
numbers that exceed the manufacturer?s published instructions.
(2) In no case shall more than 18 initiating devices be interconnected
(of which 12 can be smoke alarms) where the
interconnecting means is not supervised.
(3) In no case shall more than 64 initiating devices be interconnected
(of which 42 can be smoke alarms) where the
interconnecting means is supervised.