wire monk

Member
Is it a code violation to hardwire 1000 watt m/h fixtures in a large warehouse.. I was told they have to have a plug and recp.. They are 480 volt. 3 phase.
 

ronmath

Senior Member
Location
Burnsville, MN
I don't think so, see 410.24 (A). They are "permitted" to be cord connected per 410.62 (C). It might be a specified requirement or Owner requirement however for ease of maintenance.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
They are allowed to be hardwired If they are connected by a cord, it must be cord & plug (with exceptions).
You mentioned 480v. Hopefully the service is 480/277 or you will be in vioation of 210.6(D).
 

izak

Senior Member
Location
Springfield, MO
are you sure that they are 3 phase?
and not single phase (2 pole breaker) ?

ive not seen any 3 phase lights, and cannot think of a reason why one would need one.....
 

RUWired

Senior Member
Location
Pa.
I have to ask this because it could apply to the op's question. Does 410.130(G)3 apply to 410.130(G)1 or does it apply to 410 part XIII?

Rick
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have to ask this because it could apply to the op's question. Does 410.130(G)3 apply to 410.130(G)1 or does it apply to 410 part XIII?

Rick

interesting :D
the section could have been arranged better with "flourescent" in the heading.
I certainly may be wr.. wr.. wrong (not uncommon) but I'd say (3) is in reference to (1) and only includes flourescent fixtures with double-end lamps but my thoughts may be biased.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
If you can't cord whip into a fixture without a recep, then I've created A LOT of violations.

Low bays I always cord-and-plug though. A lot easier to reballast on the ground.
 

wire monk

Member
the service is 480/277 v they are hook up to a 2 pole breaker they have a rubber cord attached to them.. do you need to put a cord cap andrecp?? are can you run the rubber cord to a box and mc cable from box to box.
 