Harmonic Loads
Re: Harmonic Loads
Originally posted by wannabe:
what is considered a harmonic load
I think you may be asking about nonlinear loads, a nonlinear load creates harmonic currents.
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
The current leads or lags the voltage sine wave instead of following it.
Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
[ August 08, 2005, 06:44 AM: Message edited by: iwire ]
Re: Harmonic Loads
Bob, you have a dood definition of "non-linear" and a good list of non-linear loads, but I fear that I must disagree with your example, your explanation, of the term "non-linear."
Good definition. But please note that it is talking about the SHAPE of the wave form, not its timing. If you start with a clean sine wave for voltage, and if the current looks like a square wave (or more likely it will look like a messy collection of spikes and dips that only vaguely follows a sine wave pattern), then this fits the definition of non-linear.
Originally posted by iwire: The current leads or lags the voltage sine wave instead of following it.
If the current is a pure and clean sine wave, and if it lags the voltage (itself also being a pure and clean sine wave) by some amount of time, then you would not be looking at harmonics, and the load would not be "non-linear." Rather, what you would have here is a linear, but inductive, load, such as a motor.
Re: Harmonic Loads
By the way, the correct parts of my post I liberated from the NEC, the incorrect parts where all me. :D