In three phase 4-wire, it carries the sum of the triple-n harmonics. At three times supply frequency they are bound to end up in phase. That's what contributes to overloaded neutrals.
You may have missed the situation that electrofelon was talking about and I was replying to: a three phase three wire MWBC, not a full boat.
There are two phase conductors and a neutral from a three phase source.
I was in fact mistaken about the added harmonic current in the neutral, it would not be three times the phase harmonic current, since only two phases are involved in the circuit. But it would be twice the harmonic current rather than identical to the harmonic current as I originally proposed.
So electrofelon is IMHO correct in his statement that the effect of harmonic current could indeed be more of a problem in a fully loaded 2 of 3 phase plus neutral MWBC than in the corresponding fully loaded full boat as long
as the full boat did not use a reduced neutral.
If each phase to neutral load had a 30% (amplitude) third harmonic content the neutral of the 2-of-3 would be loaded to 130% of the phase current, just not 160% or 190%. By contrast the full boat would have a 90% neutral load, so a
reduced neutral, as allowed for a linear full boat would be grossly overloaded, while the neutral of the 2-of-3 would be loaded to 130% instead of the 100% it is required to carry.