Mark, thanks for the link, I hope I wasn?t coming across as cynical, just pointing out the fact of the source. I am aware of the practices of IEEE 1100, 519, and 142. In fact, I used to religiously follow the practices without question.
After working for MCI and being involved with data center and telephone office power design for several years, I have been fortunate enough to collect a lot of data, and see the industry evolve. In the 80?s & 90?s the practice of over sizing (over 100%) the neutral was a sound practice. But since that time UPS and high-end equipment manufactures have integrated power factor correction technology into there equipment, therefore negating the need in most cases.
In all my collection of data I have found maybe 2 or 3 cases where neutral current exceeded phase currents, and a couple of isolation transformers (non "K" rated) that were overheating from harmonics. As a result I have come to reexamine my own practices I have used for so many years, and have adjusted to the changing technology using what I think is sound principles.
1. 3-phase 4-wire service at 480 or higher and dead-end the grounded service conductor at the service entrance.
2. Segregate critical and non-critical feeders.
3. HVAC, UPS, and DC power plants fed delta 3-wire + EGC.
4. General receptacles fed using a low ?K? isolation transformer and full size dedicated neutral.
5. Critical loads from UPS distributed via PDU?s using full size neutral if needed.
6. Continue to push equipment manufactures into cleaning up the power by using power correction technology and/or filters.