wirenut1980
- Plainfield, IN
Hello, I have a situation on a transmission line fed from 2 sources. When the stronger of the two sources is switched out, there is high voltage distortion (between 5 and 7% voltage THD) on the transmission. Most of the voltage distortion is 17th harmonic. When both sources are switched in, voltage distortion is low (1-2% voltage THD), and the 17th harmonic is not the dominant harmonic present, more typical 3rd, 5th, 7th, etc are dominant. I have determined a large transmission fed customer is responsible for the 17th harmonic current and they are exceeding IEEE 519 current distortion limits under any switching scenario.
At first I thought I had a resonance around the 17th harmonic, but I could not get my ETAP model to agree with me :blink:
My question is would the higher source impedance (due to the stronger source being switched out) cause higher order harmonics to distort the voltage more than lower order harmonics? For example, if I measured the same amount of 5th harmonic current as 17th harmonic current, would there be more 17th voltage distortion than 5th? I think the answer is yes since the voltage distortion would be dependent on source impedance, and the inducatance part of source Z increases as frequency increases. But is that increase in voltage distortion linear as the harmonic frequency increases? Or is it a larger effect/increase?
Or do you think there is a resonance? There are no capacitors on the 138 KV line, although there are multiple distribution capacitors fed from substations along the 138 KV line.
Thanks!
Thanks!