joeyww12000
Senior Member
- Location
- Chatsworth GA
Why does sharing neutrals cause potential problems with electronic ballasts?
I think you are being misinformed.joeyww12000 said:Why does sharing neutrals cause potential problems with electronic ballasts?
and often twice the phase current.
Theory vs. Reality... the source of a lot of disinformation.brian john said:Though I have never seen this on lighting multiwire circuits.
Possible... but highly improbable, IMO.dbuckley said:Because on a polyphase system with non-linear loads the triplen harmonics add, which can cause the neutral current to be greater than any phase current, and often twice the phase current.
Thus your 100% rated neutral may overheat through overloading.
But then again, that's not exactly a graph of an electronic ballast lighting system... :grin:brian john said:ZACTLY
But then again Not twice the phase current, but HIGH
Like all most all information about the problems caused by harmonics, this one is written by a company that has a vested economic interest in solving or detecting the problem. I am not saying that they don't exist, but they are not near as big of a problem as you are led to believe they are.cripple said:You might want to look this web page; harmonics are real and here to stay.
http://www.dranetz-bmi.com/pdf/harmonicsall.pdf
winnie said:I'd suggest not turning this into a 'shared neutral' versus 'separate neutral' debate, and just focus on the issue of harmonics.
To the extent that harmonics are an issue, running separate neutrals to the various branch circuits will not change the harmonic neutral loading of the transformer in a significant way. The triplen harmonics will add up, on the common neutral of the MWBC, or if you don't use MWBCs, then they will add up at the neutral bus of the panel, and if you have separate panels for each phase, they would add up at the transformer X0 terminal.
If you wanted to eliminate the issue of triplen harmonics, then you could use single phase systems, with or without MWBCs, as you prefer. (Note, in this case by 'single phase' I am specifically excluding 'network' services derived using two legs of a three phase wye service.)
I tend to agree that they are more of an issue in theory than in practise, there are infrequent reports of neutral overloading caused by harmonics. While we are seeing more and more switching power supply loads, more and more of these loads are being designed with power factor correction, specifically to avoid the harmonics issues.
-Jon
brian john said:76:
The separate neutral will do nothing to protect the transformer, the 3rd harmonics will still be there.
cripple:
If I sold harmonic analyzers I'd be pushing the product hard (as Don pointed out). I have been doing harmonics surveys since the word became prevalent in the late 70's. In all those years, I have seen 4 or 5 major issues* on utility and maybe 20 or more while connected to a generator. And none to date have been from lighting branch circuits.
In addition my firm perform IR surveys, scanning 1000's of lighting panels a year most utilizing multi wire branch circuits, all thermal issues noted are from improper phasing of the conductors.
*most of these issues are from early UPS's, large printing presses with multiple frequency drives on under sized distribution systems, casinos (electronic slots) and call centers.
Isn't that better than jeopardizing overheating the tranny
Can you cite a documented study of a real world installation, outside of a data center, that has had a problem because the grounded conductor was not larger than the ungrounded conductors?76nemo said:Brian,
Undersized neutrals ARE a problem. I am not sure what exactly you are trying to point out:-?
If I sold harmonic analyzers I'd be pushing the product hard (as Don pointed out).
I have been doing harmonics surveys since the word became prevalent in the late 70's. In all those years, I have seen 4 or 5 major issues* on utility and maybe 20 or more while connected to a generator. And none to date have been from lighting branch circuits.
In addition my firm perform IR surveys, scanning 1000's of lighting panels a year most utilizing multi wire branch circuits, all thermal issues noted are from improper phasing of the conductors.
don_resqcapt19 said:Can you cite a documented study of a real world installation, outside of a data center, that has had a problem because the grounded conductor was not larger than the ungrounded conductors?
pbeasley said:If the dimming system is loaded to capacity, then the neutral feeders should be doubled to accommodate.