Have you ever seen this in attic?

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I seen something that to me looked bad. It appears to be an AC micro inverter install with this going thru attic. It appears that AC string output penetrates directly into attic and combines on a roof box with greenfield out back of box then from attic to outside of house.

I guess romex in attic is ok it appears to go to roof box being AC but install looks terrible.
 

Attachments

  • 794CFA57-A8E6-4967-AAA5-B3F39F776079.jpeg
    794CFA57-A8E6-4967-AAA5-B3F39F776079.jpeg
    87.4 KB · Views: 57
  • 38E4C354-C315-46CD-AF52-5AD173F54E59.jpeg
    38E4C354-C315-46CD-AF52-5AD173F54E59.jpeg
    76.5 KB · Views: 56
  • 504A4E79-DB73-40E3-BEC0-E2FFBE3F22EB.jpeg
    504A4E79-DB73-40E3-BEC0-E2FFBE3F22EB.jpeg
    97.7 KB · Views: 56

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Yes it is a sloppy job for sure and probably not to code. What is that white tape or marking on the orange cable in the 2nd picture?
Appears to cover a Knick. I guess since the romex goes to a rooftop box if you want to be picky that could be a violation. Just looked terrible
 

Electrical Geek

Lead PV Service Electrician
Location
Massachusetts
Occupation
Electrician
Other than being a sloppy install, (and that definitely is) it's not against code to run NM cable to a roof box for a microinverter system. It also doesn't have to be marked because it's an ac system.
 