If I am reading correctly he is saying they tape conductors of same circuit together throughout the run.
Makes it difficult to "pull one out and one (plus additionals) back in" later on, or even to pull individuals when trying to make things up at a pull box or conduit body.
Dunno about taping throughout the run vs ends, but having effectively done that a few times pulling large amounts of staggered catx cable, if you dont pull all the cable taught and dead straight when taping, and tape the middle points, you're right, you wind up with a huge unpullable mess when navigating corners/sweeps/bends, like driving a vehicle in 4WD with differential locks engaged.
The way I'd do it:
Say I'm pulling 3 MWBC with EGC to 3 boxes, staggered ~ 10' apart. #14 in 1/2" EMT. First or lead head has 2 hots, neutral, and EGC. Mark wires with pliers. Tape together (Tape joint #1), rig onto string line.
Pull off 10', set head into something so it's tight (Or have helper hold it), grab 3 more wires (2 hots and neutral), mark wire with pliers, tape them together, then rig onto the string line (tape joint #2) Then, pull 10' more and repeat that last step (tape joint #3). 10 conductors.
Pull from panel to first box, then pull out 20', to get to shortest/last stagger (tape joint #3). All 10 wires out of the box. Remove last 3 wires at that point from string, pull extra 6' on EGC. feed remaining 7 back in to second box, pull out at 2nd box, undo 2nd stagger, pull extra 4' of EGC. Feed remaining 4 wires/initial lead head back into the conduit, pull to 1st box and out 2'.
At this point all the wire is basically taught, there is 2' working length at each box, no tape in the conduit. As far as the reels go, I rig the pulls so that the first box's wire would be on shaft #1, or the left side of a single shaft, the 2nd box in the middle/#2 shaft, 3rd box on the right/#3 shaft. Tape wires together, mark them, cut off wire from reels. This method works for me up to 25 wires/cables at a time; for catx, I've set up pull boxes 4 wide and 5 high, with all the rolls of coax on a piece of IMC rolling in a set of D-rings I've mounted to the studs in the hallway.
Didn't mean to turn this into a thread on wire pulling but in the end, I wind up with no tape in my conduits and correctly identified wire. Had I taped everything together along the run, getting slack on the EGC would be impossible. Aside from staggers, taping in the middle adds time and difficulty to the pull and absolutely nothing positive - it is utterly pointless.