Hmm... is there even such a thing as a non-pvc-coated one?vvalerio said:Can anyone tell me if any manufacturers makes an explosion proof expansion deflection fittin that's PVC coated??? Can't fiond one.
vvalerio said:Can anyone tell me if any manufacturers makes an explosion proof expansion deflection fittin that's PVC coated??? Can't fiond one.
Hmm... under what division?weressl said:Rob Roy is the only approved one that I know.
Please describe the reason you believe you need an explosion-proof expansion/deflection fitting?vvalerio said:Can anyone tell me if any manufacturers makes an explosion proof expansion deflection fittin that's PVC coated??? Can't fiond one.
Smart $ said:Hmm... under what division?
I checked under Perma-cote, Plasti-bond, and Korkap expansion fittings and they are all UL Listed under Standard 514B only, which states in part:Conduit, Tubing, and Cable Fittings
1 Scope
...
1.4 These requirements do not cover FITTINGS intended for use in hazardous locations as defined in the National Electrical Code, ANSI/NFPA 70, the Canadian Electrical Code (CEC), Part I, CSA C22.1, and the Standard for Electrical Installations, NOM-001-SEDE.
How so? Only UL 514Bdon_resqcapt19 said:Smart,
...that one can be used in a Class I, Division 2 area.
OK. I concede the indicated expansion fitting is permitted in C1D2 locations.don_resqcapt19 said:In most cases, Class I, Division 2 areas do not require the use of explosionproof fittings.
Compare the 501.10(A)(3) with 501.10(B)(4).
Yes, the term "explosionproof" was used, but I find that term is often tossed about and in many cases the area is in fact a division 2 area.Smart $ said:OK. I concede the indicated expansion fitting is permitted in C1D2 locations.
But getting back to the OP, we need to establish the classification of the location where such would be installed. After all, the request was for a PVC-coated explosionproof expansion/deflection fitting.
don_resqcapt19 said:Yes, the term "explosionproof" was used, but I find that term is often tossed about and in many cases the area is in fact a division 2 area.
Yeah... but how much electrical apparatus do you think is gonna get put in an expansion fittingweressl said:The two terms are not mutually exclusive.
Whenever the electrical apparatus represents a source of ignition in the course of its normal operation it must be 'explosionproof'-ed, even in Division 2 areas.
Smart $ said:Yeah... but how much electrical apparatus do you think is gonna get put in an expansion fitting![]()
Hmmm... I believe you are referring to Don's statement. Regardless, the discussion has pretty much remained on topic, that being pvc-coated explosionproof expansion fitting, and the sub-topic of whether or not an explosionproof [expansion] fitting was required. Let's not steer it off-topic.weressl said:Your statement was not exclusive to the expansion fitting, but generalized.![]()
Smart $ said:Hmmm... I believe you are referring to Don's statement. Regardless, the discussion has pretty much remained on topic, that being pvc-coated explosionproof expansion fitting, and the sub-topic of whether or not an explosionproof [expansion] fitting was required. Let's not steer it off-topic.![]()
Quote:
Originally Posted by don_resqcapt19
Yes, the term "explosionproof" was used, but I find that term is often tossed about and in many cases the area is in fact a division 2 area.
The two terms are not mutually exclusive.
Whenever the electrical apparatus represents a source of ignition in the course of its normal operation it must be 'explosionproof'-ed, even in Division 2 areas.