hazardous spaces
sleepy
need info on hazardous spaces
we have materials such as acetone,tolueone,xylene plus others
where can i find info on how far away from material is the most stringent
how high above the materials is the most stringent
this type of info
thanks for your help
your best bet is to buy a good book on the subject. i think nfpa has one. can't recall its name. maybe bob alexander can tell us.
The book Bob (petersonra) is referring to is Electrical Installations in Hazardous Locations, by Peter J. Schram and Mark W. Earley.
The biggest problem we usually have in answering electrical area classification (rather than electrical installations in classified locations) questions in this forum is there is often not enough detail about the processes involved. In other words, are you manufacturing, storing large quantities, simply "using" relatively small amounts of ??acetone, toluene, xylene plus others,? etc. They could each result in different electrical area classifications from none to Division 1, depending on the conditions
Electrical area classification is simply not a trivial exercise.
The most likely applicable Standard is NFPA 30, Flammable and Combustible Liquids Code, especially chapters 1, 7, and 8. If you are dealing with a manufacturing process then NFPA 497 is probably the better document.