We are doing a hospital addition.

Is it permissable to rough in under a slab on grade with PVC ( in stead of meatal conduit) in patient care areas if a redundant ground is pulled in the PVC?

Section 517
 

jim sutton

Senior Member
Re: Health Care Facility

sorry, meant to say HCF cable which is basically MC cable with the armor rated for grounding.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Health Care Facility

Jim is correct, read 517.13(A), there is no exception for Patient Care Areas.

Roger
 