B bjohn New member Apr 27, 2005 #1 We are doing a hospital addition. Is it permissable to rough in under a slab on grade with PVC ( in stead of meatal conduit) in patient care areas if a redundant ground is pulled in the PVC? Section 517
We are doing a hospital addition. Is it permissable to rough in under a slab on grade with PVC ( in stead of meatal conduit) in patient care areas if a redundant ground is pulled in the PVC? Section 517
J jim sutton Senior Member Apr 27, 2005 #2 Re: Health Care Facility To me, 517-13 says no. GRS in slab or use EMT or HFC cable in walls and ceiling.
Re: Health Care Facility To me, 517-13 says no. GRS in slab or use EMT or HFC cable in walls and ceiling.
J jim sutton Senior Member Apr 27, 2005 #3 Re: Health Care Facility sorry, meant to say HCF cable which is basically MC cable with the armor rated for grounding.
Re: Health Care Facility sorry, meant to say HCF cable which is basically MC cable with the armor rated for grounding.
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 27, 2005 #4 Re: Health Care Facility Jim is correct, read 517.13(A), there is no exception for Patient Care Areas. Roger
Re: Health Care Facility Jim is correct, read 517.13(A), there is no exception for Patient Care Areas. Roger
C cosmos Member Apr 29, 2005 #5 Re: Health Care Facility Intent is redundant ground paths - metallic conduit AND seperate ground wire.
Re: Health Care Facility Intent is redundant ground paths - metallic conduit AND seperate ground wire.
peter d Senior Member Location New England Apr 29, 2005 #6 Re: Health Care Facility Originally posted by jim sutton: sorry, meant to say HCF cable which is basically MC cable with the armor rated for grounding. Click to expand... HCF is Type AC cable, not MC cable.
Re: Health Care Facility Originally posted by jim sutton: sorry, meant to say HCF cable which is basically MC cable with the armor rated for grounding. Click to expand... HCF is Type AC cable, not MC cable.
J jim sutton Senior Member Apr 29, 2005 #7 Re: Health Care Facility Thanks Peter, for the correction.