I am currently looking at a project in a Kidney Dialysis Clinic. No anethesia, 12th Floor of an Office Building definitely doesn't have a life safety or critical branch.

Do the receptacles that are to be installed need to be Hospital Grade? There are no specifications on the project and I can not find this requirement. Does the wiring need to be Hospital Grade MC or conduit/wire with ground?

I believe that it does need to be wired in accordance to Article 517, but the GC that I am bidding to is not requiring it from the other bidders.

Just wondering what you think.

Thank you,
John
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Kidney Dialysis Clinic.

Sounds like a health care facility to me. Check out the definition of health care facility in 517.2

Does the wiring need to be Hospital Grade MC or conduit/wire with ground?

The wiring method employed in the patient care areas need to comply with 517.13.

Chris
 

iwire

Moderator
Staff member
Location
Massachusetts
gardiner said:
You might want to check with the local inspection department as to how they will classify the project.

I would agree with that if the NEC did not provide a clear definition of a Health Care Facility.

517.2 tells us in part that portions of buildings in which medical, nursing care is provided are Health care facilities.
 