I'd put a reactor on the load side of the drive, especially with 480 volt system.
Also did you mention what frequency the motor typically runs at (other then the one minute no speed period occasionally)? I though you did but am not finding it. More important is does it run for long periods at low speeds, you can get away with more on fans and pumps as they are variable torque, but constant torque loads don't like the reduced cooling effects from the slower fan speed when the torque level is still high. I had to put a VFD rated motor with external cooling fan on a high pressure pump because we only were running that thing at about 30 Hz a lot of the time. Rewound a 50 Hp motor on that one 3 or 4 times, each time about a year had passed, before switching to the new motor - haven't had a failure yet and it has been there maybe close to 10 years now. Never have had a load side reactor on that one either - though the distance was probably in the 50 foot range. Think I would put one on it if I were doing it today though.
43 hz with ON time of about 8-15 minutes, OFF time of 6-12 minutes. Eight to ten cycles of ON/OFF. End of day, motor runs @ 58 hz for about 50 minutes.