If I came up with a heat detecting outlet that would shutoff power to device from excessive heat, would this be something that manufacturers and the NEC might pass on a future code cycle?
 

Cletis

Senior Member
Location
OH
Fuses and Arc Fault breakers wont catch glowing connections though, I mean a rec with a sensor in it to detect heat in that outlet
 

Cletis

Senior Member
Location
OH
I noticed that too. They probably didn't take into the account of HO's, GC's, and some electricians doing "bare minimum" and maybe were counting on it to be required in 2014 NEC. It's a great idea and I hope they can hang on and maybe get it manditory the next possible code cycle. I think it's a great idea but probably too expensive per unit
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I think it's a great idea but probably too expensive per unit
It would probably not be able to protect against maybe 50% of the most likely faults - those caused by poor connections on the line side of the device.
 

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
"Most electrical fires result from fixed wiring . . ."--is that true? I'd always heard the opposite, most electrical fires caused by the stuff that's plugged in to fixed wiring.
 

Cletis

Senior Member
Location
OH

I went ahead and took an excerpt from that link above and extrapolated a theory


  • U.S. fire departments respond each year to an estimated 25,900 home electrical fires. These fires cause an estimated 280 deaths, 1,125 injuries and $1.1 billion in property loss.
  • Thirty-nine percent of home electrical fires involve outlets and receptacles, electrical branch circuits (for example, interior house wiring), and other electrical wiring.
Therefore, 39% of above would be

10,101 House Fires

109.2 Deaths

438.75 Injuries

0.429 Billion in Damages

Sounds like enough evidence to pass something like this to me?
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
I went ahead and took an excerpt from that link above and extrapolated a theory


  • U.S. fire departments respond each year to an estimated 25,900 home electrical fires. These fires cause an estimated 280 deaths, 1,125 injuries and $1.1 billion in property loss.
  • Thirty-nine percent of home electrical fires involve outlets and receptacles, electrical branch circuits (for example, interior house wiring), and other electrical wiring.
Therefore, 39% of above would be

10,101 House Fires

109.2 Deaths

438.75 Injuries

0.429 Billion in Damages

Sounds like enough evidence to pass something like this to me?

The data is insufficient to tell us how many fires were caused by overheated receptacles.

The heat sensing receptacle will do nothing to stop fires from overheated extension cords or permanent wiring or overloaded circuits, which likely cause far more fires than anything happening at a receptacle inside a box.

The only time I have seen a receptacle actually get hot enough to catch fire it was used as a pass through. Pigtailing would have prevented the incident. The fire burnt through the side of the receptacle and smoke stained the wall above the cover, but no damage to the structure. When the receptacle burned, it melted a wire and shut the power downstream off.

On the same circuit I found one more receptacle that was getting hot enough to melt the plastic, but still worked. One screw terminal was loose, probably from years of thermal cycling. That was also used as a pass through ahead of where the space heater was plugged in.

A better code change would be to not allow receptacles to be used as pass through devices.
 

Cletis

Senior Member
Location
OH
The data is insufficient to tell us how many fires were caused by overheated receptacles.

The heat sensing receptacle will do nothing to stop fires from overheated extension cords or permanent wiring or overloaded circuits, which likely cause far more fires than anything happening at a receptacle inside a box.

The only time I have seen a receptacle actually get hot enough to catch fire it was used as a pass through. Pigtailing would have prevented the incident. The fire burnt through the side of the receptacle and smoke stained the wall above the cover, but no damage to the structure. When the receptacle burned, it melted a wire and shut the power downstream off.

On the same circuit I found one more receptacle that was getting hot enough to melt the plastic, but still worked. One screw terminal was loose, probably from years of thermal cycling. That was also used as a pass through ahead of where the space heater was plugged in.

A better code change would be to not allow receptacles to be used as pass through devices.

Actually, I agree with you. Your onto a great idea. What about incorporating receptacles 120V 15 and 20 amp cannot be used for pass through power? Maybe get ahold of levitan or PnS and have them go for a 2 screw (1 hot, 1 neutral) device with no back stab holes either ???
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Actually, I agree with you. Your onto a great idea. What about incorporating receptacles 120V 15 and 20 amp cannot be used for pass through power? Maybe get ahold of levitan or PnS and have them go for a 2 screw (1 hot, 1 neutral) device with no back stab holes either ???

I only have control over what I do. I am not good at trying to get rules changed. Not only that, there are many electricians on this site that think backstabbing and passing through are just fine.

I am also going to invest in a torque screwdriver so the receptacle screws are all torqued to spec. If the instructions call for a torque spec and it was ignored, that is a NEC violation. How many sparkies do you know that use a torque screwdriver?

Would the failures I witnessed had not occured if the screws were torqued properly upon installation? I am going to say no, they would have been fine.

Adding NEC rules because the ones that are already in place aren't being followed is really counterproductive.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Here, like this one i've created

I appreciate your ingenuity, but all that will happen is that one screw will be used for two wires. I see it all the time on two screw receptacles with three cables going to them.

Remember, the Universe is winning.

Edit to add:

Change the design to a single wire backstab and use the same technology Wago does and you may be on to something. Selling it.....I don't know if EC's would find them all that appealing.
 
Last edited:

lunalilo

Member
"Most electrical fires result from fixed wiring . . ."--is that true? I'd always heard the opposite, most electrical fires caused by the stuff that's plugged in to fixed wiring.
I believe "fixed" also includes wiring that has been messed with, for example every moved light fixture, and wires that have not been properly contained.

I think it also includes broken receptacles and outlets also. And let's not forget corrosion.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
I believe "fixed" also includes wiring that has been messed with, for example every moved light fixture, and wires that have not been properly contained.

I think it also includes broken receptacles and outlets also. And let's not forget corrosion.

In this case, I believe 'fixed' means permanently attached, as opposed to extension cords which are not. At least they aren't supposed to be.
 

Cletis

Senior Member
Location
OH
All it takes is 1 kid to be killed in a school shooting to change all kinds of laws and rules. I would think at least 2 kids have been killed by a backstab, and that's being extremely conservative
 