I have never been clear if branch circuit selection current and minimum circuit ampacity are the same. Like others, I have never seen a unit marked with branch circuit selection current. I am however firmly in the camp that says MCA means just that-you need conductors with the stated MCA and the max. breaker can be as stated. I am often amazed how many otherwise experienced electricians don't follow this concept. Even more shocking is the number of inspectors who don't understand this concept and insist that the conductor ampacity must be sized to the overcurrent device. Any inspectors care to comment?