- Location
- New Jersey
- Occupation
- Journeyman Electrician (retired)
I have a heat pump that has an MCA of 21.7 amps and a unit switch pre-wired with two tails for connection to the branch circuit. The branch circuit is #12 MC cable fed from a 75 degree terminal on the 2 pole circuit breaker. The unit end is connected to the wire tails with wire nuts. Is this compliant?
I say that it is but there has been some opinions that the 60 degree C ampacity of the #12 conductors must be used due to the switch terminals. IMO the switch terminals do not matter since the connection to the branch circuit is at the wire tails.

I say that it is but there has been some opinions that the 60 degree C ampacity of the #12 conductors must be used due to the switch terminals. IMO the switch terminals do not matter since the connection to the branch circuit is at the wire tails.