thomasjohnschulte
Member
At what temperature Farenheit wiil the two different electical methods become cost equal -- if ever?
Is this a textbook question or reality question?At what temperature Farenheit wiil the two different electical methods become cost equal -- if ever?
For that consideration, you should model heat pump versus gas heat if you have access to reasonably priced gas. A 95% efficient condensing furnace will beat a heat pump for equivalent BTU output if the COP drops much below 3, so your climate zone matters.Is this a textbook question or reality question?
In reality:
If by cost you mean only the amount of electricity used, they will never be equal as long as the heat pump can function. See Jon's post. The heat pump will always use less electricity until it can't be used anymore. So the answer to the question, more or less, is when the temperature Farenheit is below the heat pump's specified lowest temp.
If you mean the total cost to install and use, say for new construction, that would require a economic model with inputs of cost, performance, and forecast usage and temperatures. You could spend a whole career developing that, and it would still provide only best guesses.
I took a quick peak at Mitsubishi's web site, and the concept is VFD for heat pumps. Instead of bang-bang control, it's PID so the equipment is running all the time.I recently was told that there is an "inverter heat pump" (the term used by the electrical contractor who told me about it) that can operate at much lower ambient temperatures than heat pumps that do not use that tech. And that is 100% of what I know about them.
"Inverter heat pumps" have been available for decades in the higher-end market segments.I recently was told that there is an "inverter heat pump" (the term used by the electrical contractor who told me about it) that can operate at much lower ambient temperatures than heat pumps that do not use that tech. And that is 100% of what I know about them.
Yes, they're still trying.I think many/most/all mini splits don't shut down when their "lowest" outdoor temp is reached, rather they will no longer produce their full nameplate heat output
That seems like an opportunity for something vital to go "sproing!"I think many/most/all mini splits don't shut down when their "lowest" outdoor temp is reached, rather they will no longer produce their full nameplate heat output
I don't see why, there's just a bit less heat in the air to suck out. I mean we all know you hate anything that doesn't run on gasThat seems like an opportunity for something vital to go "sproing!"
Do you understand how HVAC compressors work? If there isn't sufficient heat to vaporize the refrigerant on the expansion side, you run the risk of slugging the compressor with liquid refrigerant. Any liquid is incompressible at HVAC pressures, and you'll bust the compressor, or if you're lucky pop some overpressure device which will still shut down the unit.I don't see why, there's just a bit less heat in the air to suck out. I mean we all know you hate anything that doesn't run on gas![]()
Yes, I am sure they design these things to just self destruct under certain conditions.Do you understand how HVAC compressors work? If there isn't sufficient heat to vaporize the refrigerant on the expansion side, you run the risk of slugging the compressor with liquid refrigerant. Any liquid is incompressible at HVAC pressures, and you'll bust the compressor, or if you're lucky pop some overpressure device which will still shut down the unit.
It's not necessary to fill the compressor with liquid to damage it, or to hit it with a large slug of liquid.Do you understand how HVAC compressors work? If there isn't sufficient heat to vaporize the refrigerant on the expansion side, you run the risk of slugging the compressor with liquid refrigerant. Any liquid is incompressible at HVAC pressures, and you'll bust the compressor, or if you're lucky pop some overpressure device which will still shut down the unit.
Each time the temperature drops below 30°F?My heat pump turns itself off around 30F, so I remove the T-stat and jumper from red to yellow.
Don't know about Richmond VA but in Richmond CA that'd be about once every two years. Probably feasible.Each time the temperature drops below 30°F?