I am sorry but where does either E or G specifically permit this?
I am out.
This is all well established, it is blowing my mind you are not seeing it.
I am sorry but where does either E or G specifically permit this?
I am out.
This is all well established, it is blowing my mind you are not seeing it.
I am sorry but where does either E or G specifically permit this?
Agreed. Which table does 440 say to use? 440 allows you to upsize the OCP not downsize the required ampacity.Per Art. 440, the equipment in the OP requires a conductor with an ampacity of at least 22 and allows the conductors to be protected at not greater than 35A.
Agreed. Which table does 440 say to use? 440 allows you to upsize the OCP not downsize the required ampacity.
Agreed. Which table does 440 say to use? 440 allows you to upsize the OCP not downsize the required ampacity.
And #12 THHN or THWN has an allowable ampacity of 25 at 75degC...which is greater than 22.
Agreed. Which table does 440 say to use? 440 allows you to upsize the OCP not downsize the required ampacity.