Just tried out my heat pump on my my family room 800 sq feet 3 1/2 ton and very impressed on its output at 24 amps/240.Are they really more cost effective ?
Jim, you have 3 1/2 ton for only 800sq ft? I have 3 ton on a/c handling over 1600sq ft. The "rule of thumb" I have always been told is 1 ton per 800 sq ft. I am also assuming that your location you do not have heat strips in the unit etherJim W in Tampa said:Just tried out my heat pump on my my family room 800 sq feet 3 1/2 ton and very impressed on its output at 24 amps/240.Are they really more cost effective ?
dereckbc said:When you compare btu's between a heat pump vs electric strip heat for a given kilowatt, the heat pump wins out by about a 3 to 1 ratio say above 45 degress outside air temp. However by the time the temp drops to 32, the ratio is equal. Below 32 the heat pump looses the battle, and below say 20 is useless.
dereckbc said:Jim that is a bit of a hard question to answer because it depends on many factors most importantly cost of gas vs electricity, and the temp differential between outside air and inside.
However I will fgo out on a limb here since I believ you are in Tampa FL, a heat pump is your most economic heat source. I base that on your are is highly unlikely to ever drop below 35 degrees and need backup heat.
When you compare btu's between a heat pump vs electric strip heat for a given kilowatt, the heat pump wins out by about a 3 to 1 ratio say above 45 degress outside air temp. However by the time the temp drops to 32, the ratio is equal. Below 32 the heat pump looses the battle, and below say 20 is useless.
To really narrow it down you have to look at few factors, how much is your electric rate per BTU vs NG price along with the differential temp. In my area NG is dirt cheap and electric is expensive so NG heat wins out at any temp.
If you live in a northern climate, forget a heat pump unless you have dual source like heat pump when outside air is above 35, and gas backup when temps drop below 35.
Jim W in Tampa said:Just tried out my heat pump on my my family room 800 sq feet 3 1/2 ton and very impressed on its output at 24 amps/240.Are they really more cost effective ?
LawnGuyLandSparky said:I say, heat pumps should not be used ANYWHERE where electricity is higher than the national average. Once you have to suffer the installation costs of backup NG or Oil heat, the cost-benefits of a heat pump goes out the window.
You are exactly right Jim, the math does not seem to work, but there is a good explanation for the discrepancy. Your wattage (assuming a power factor of one or near one), is 24.4 x 240 = 5.86 kw. This is equivalent of around 20,000 BTU/hr, or about 1.7 tons. The fact that you get 3.5 tons from the heat pump represents a Coefficient of Performance (COP) of around 3.5 / 1.7 or about 2.1 This means you get around 2.1 units of thermal energy for every 1 unit of electrical energy spent. Strange as it sounds, it does not violate conservation of enery law, as you are using the electric energy to simply move heat from one place to another, and not converting electric energy to heat directly. Ground source heatpumps are even more impressive than this, as they have a much better COP than the air-source heatpumps. Heat pumps are almost always cheaper than resistive electric heating (they degrade to the efficiency of resistive heating, once the auxiliary heat comes on in very cold weather). e/mJim W in Tampa said:In Tampa i will seldom dip under 50 and usuallynot even that cold.The 3 1/2 tons are because of the large crouds we entertain ,sometimes up to 70.The fan has multi speed to back its over kill down as needed.Also has heat strip if needed.I simply was surprised at amount of heat while only pulling 24 .4 amps /240.Electric here is from progress energy and is about 12 cents per kw
Cavie said:Having been in the a/c business, I do not think you have 3.5 tons in 800 sq ft. If you do, you got the shaft and the a/c is not gonna work. It will turn on for about 5 min, cool of the room and shut off. You willl not get any dehumidification. Sized right, they are very effeicant. Your is not because 3.5 ton will heat and cool a 2800 sq ft house.
The pole alone will probably consume half of the cooling capacity...Jim W in Tampa said:I agree its too large but i did the install myself.I run a small club and it gets packed with couples and it has a dance floor with a pole for the girls.Also must deal with the slider door to hot tub area will get opened often.Once its cooled down the main house AC 3 ton keeps it to 76.All totalled i am cooling almost 2900 sq feet,half of it 24/7 rest only on saturday nights.Its very importand to be able to keep the people feeling cool.My AC friend has suggested i run the blower at slow speed to help.Heat pumps are new to me so really had no idea what to exspect.My 10 kw on main house never put out near this much heat.
Well I am not going to say much about that, but you earlier said crowds of 70 people. With that many people in such a small space shouldn't require any heat.Jim W in Tampa said:I agree its too large but i did the install myself.I run a small club and it gets packed with couples and it has a dance floor with a pole for the girls.
dereckbc said:Well I am not going to say much about that, but you earlier said crowds of 70 people. With that many people in such a small space shouldn't require any heat.![]()
Jim W in Tampa said:Actually its because of body heat that you need to increase the AC size.And with the added antifreez (drinks) few will get cold.Heat is mainly needed for the clean up work next day.
I read somewhere that average person puts out equivalent of 80 watts of heat when at rest. The amount output goes to near 150 watts when exercising (e.g. dancing). Based on this, and figuring 100 watts average per person and 70 persons present, it is 7 kw, or a little over 2 tons of heating capacity. Not bad considering it is free heat source! e/m.Jim W in Tampa said:Actually its because of body heat that you need to increase the AC size.And with the added antifreez (drinks) few will get cold.Heat is mainly needed for the clean up work next day.
Energy-Miser said:I read somewhere that average person puts out equivalent of 80 watts of heat when at rest. The amount output goes to near 150 watts when exercising (e.g. dancing). Based on this, and figuring 100 watts average per person and 70 persons present, it is 7 kw, or a little over 2 tons of heating capacity. Not bad considering it is free heat source! e/m.
I must be a high-efficiency unit. I rarely wear a jacket outside, I'm always warm indoors, and when PJ puts her cold feet on me, we both say, "Ahhh!" She calls me her electric blanket.Energy-Miser said:I read somewhere that average person puts out equivalent of 80 watts of heat when at rest. The amount output goes to near 150 watts when exercising (e.g. dancing).
It's not free at all. You have to feed the generators: Wings, chips, quesadillas, etc., etc., etc.Based on this, and figuring 100 watts average per person and 70 persons present, it is 7 kw, or a little over 2 tons of heating capacity. Not bad considering it is free heat source! e/m.