thank ya all... there was something written in a manufacturers guide that was a bit
confusing, and the resistance of something is not a function of the voltage applied,
and if ya double the voltage, the current doubles as well....
had a length of heat trace cable, supposed to be 5 watts a foot nominally... was
initially going to be 100', turned out to be 190' or so... now, if it's self regulating
cable, 5 watt a foot will draw up to 8 watts per foot until the temperature comes up
to 100 degrees or so....
so initially, 8 x 190' would be 1,590 watts, tapering down to 950 watts at operating range....
said cable, on 117 volts, is drawing 24.5 amps, or 2866 watts. current flow is staying constant.
something to investigate.....