FWLIW, a friend of mine has a half dozen of these, plugged into conventional GFCI receptacles, and with no problems from nuisance tripping.
Keep in mind the heat cable can still be within it's specifications and have leakage high enough to trip class A GFCI device. Longer the cable run the higher that risk is, you possibly have short enough runs it is not an issue. I have used class A GFCI on many condensate drain heat cables, many only being 10 feet or less and never had nuisance trip trouble with them either.FWLIW, a friend of mine has a half dozen of these, plugged into conventional GFCI receptacles, and with no problems from nuisance tripping.
I agree with what you have said. exception in 210.8 says "Exception to (3): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment"Oh ok. I don't have my book handy, the question is is there a location requirement for the 426 GFPE? Does the branch circuit require GFPE or just the heating cable?