Heater in Diesel Fuel storage area

Status
Not open for further replies.
It is my understanding that Diesel fuel storage area falls under Class 1 Division 2. I have to purchase and install unit heaters in the ceiling. I am looking at 501.135(B)(1). If I use item 1 then I can use a 5KW unit heater which has a maximum temperature of 163 degrees Celsius through a high limit. According to what I read Diesel has an autoignition temperature of 256 degrees Celsius x 80% = 205 deg. C.

Since the heater max temp is less than 80% of the autoignition temp then I can use a regular unit heater and not a Class 1 Div 1 heater. Correct?

Note: I am replacing two existing and adding two so I wanted to make sure the original installation was correct as well.

Thank you
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Diesel has a fairly low vapor pressure and is rather difficult to ignite. Take a small pan of diesel sometime and amuse yourself dropping lit matches into it. Even with an inch or two of free board to confine the fumes, you're not likely to have any success.
 