Nardie
Member
- Location
- North Augusta, SC USA
So I have a fan motor that keeps tripping the heaters during startup, the starter is a AB 509 starter with a E100 overload relay. The starter and overload relay replaced an outdated set, and worked for a few months. Recently, when we try to start the motor the heaters trip 2-3 seconds. The motor's FLA is 25A, and the overload relay was set to 31A with a 30 second delay. During megger and continuity test between the load side of the starter and motor read good. In addition, we reterminated the motor connections and increased the FLA setting on the overload relay with no difference on the operation. No fuses blown, just the overloads tripping. We did replace the E100 relay with the same result. So what are we missing?