i have (16) p - tac units that are rated at 3.52Kw, 208v single phase each. What size of 3 - phase sub panel would i need to set?
16*3.52Kw = 56.32
56.32*1000 = 56320
56320/208 = 270.77
270.77 / 1.732 = 156a
would a 200 amp. 3 - phase panel be big enough?
16*3.52Kw = 56.32
56.32*1000 = 56320
56320/208 = 270.77
270.77 / 1.732 = 156a
would a 200 amp. 3 - phase panel be big enough?