Okay, I'll take a stab: #6 cu.Originally posted by jeffhood:
a central electric heater has a 15 kw rating and a 3/4 horsepower motor. What size subfeed cable would be required to feed a subpanel that would be used to disseminate the loads?
You can't put a panelboard in an unaccessible location.Originally posted by jeffhood:
it is an an unaccessibel part of attic about 12 " from roof line very hot
Would electric heat be a continuos load?i add 25 percent over because this will be a " contouis running device if so.
the adjustment amp factor is 86.75 amp
It does not matter.Originally posted by infinity:
Would electric heat be a continuos load?
Correct.Originally posted by wyatt:
you can't use the data plate on motors when sizing the load right? you use 430 tables
According to definition, it's a feeder:Originally posted by jeffhood:
thanks for the replies, got a question?Since the #2 xxhw will be coming from the main pnl feeding a subpanel with two 60 amp breakers in that inturn feed the heating unit do we calculate the subfeed as a branch circuit or a feeder?
Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
The former.
Also if the loads of heating have to be divided into loads not exceeding 48 amps then is it permissible to install like described above or would yuou have to install 2 seperate parrall 60 amp circuits from heating unit to main pnl.???????????????