HEIGHT OF DISCONNECT

Status
Not open for further replies.

fuseboy

Member
Customer would like me to lower 60A disconnect switches. Presently they are approximately 3FT., O.C., above grade. Is there a minimum height anyone is aware of that I must adhere to?
 
Re: HEIGHT OF DISCONNECT

In some areas of coastal Florida, we have 100-year flood plane levels. In these areas, some electrical equipment cannot be installed below that point. Check with your building code and the AHJ.
 
Re: HEIGHT OF DISCONNECT

THANKS FOR ADVICE. DISCONNECTS ARE OUTDOOR INSTALLATION FOR TRUCK DOCKS. CUSTOMER WISHES TO LOWER FOR AESTHETICS. MAY I BURY 2' T'S BELOW GRADE AND REDUCE TO 1"/ DISCONNECT ABOVE GRADE?WIRE SIZE IS 6AWG FOR VD, 3perPHASE, + 2 FOR 120V BLOCK HEATERS. AGAIN THANKS FOR THE INPUT.
 
Re: HEIGHT OF DISCONNECT

DISCONNECTS ARE FOR OUTSIDE TRUCK DOCKS. MAY I BURY PVC T AND REDUCE TO SMALLER PVC ABOVEGROUND? CUSTOMER WISHES TO LOWER DISCONNECTS FOR AESTHETIC REASONS.
 
Re: HEIGHT OF DISCONNECT

Customer wishes to lower disconnects for aesthetic reasons. Disconnects are outside for truck docks. May I bury pvc t's below grade and reduce above grade?
 
Re: HEIGHT OF DISCONNECT

If you are talking about burrying t condulets below grade.....Think of what the problems would be #1 not listed for direct burial,#2 110.26,ETC.
 